Beginners / Re: Transformer - Mains Oscilloscope Probing
« Last post by Silenos on Today at 10:44:00 am »then the RCDs of the neighboring houses will be triggeredEwww how on earth you come up with such an idea? That's why everyone has their ows sets of RCD and fuses...
Ok, let me put it straight. You never have to hack the installation in osciliscope cases, ever. And the type does not matter, either. I was just explaining you what will happen when you connect neutral with PE, and I still have no idea why you insist on doing that except the evervague "safety reasons" - it is a mistake in any case, that's all.
At least in my part of Europe neutral wire is considered "high voltage" (230/400 V) wire in the safety standards, and it is supposed to be treated like this. And in a real installation there is always some N-PE voltage floating due to return currents, hence the RCD action when connecting these wires.
Disclaimer: you would be surprised what can the PE in wall socket be connected to, especially in older households, sites, with TN-C 2-wired installations. Though no idea of such "traditions" in your area.
Ok, cut this subject, just don't mess with it.
So now some board is appearing. No idea what exactly are you going to measure. What do you mean "right values"? Measuring anything with the osciliscope will always show "false values", as you are biasing the DUT with a probe. The transformer is also a machine collapsible to iirc simple RLC/magnetic flux circuit.