Test Equipment / Re: Cheap oscilloscope for checking mains power quality? Also logging equipment.
« Last post by adam4521 on Today at 09:41:23 pm »For low cost power quality logging I've had some success using a commercial-grade electricity meter: Schneider PM5110/PM5111 for example which you can easily find used/surplus. Install into an adaptable box. Lower cost than a power quality analyser, and you can read out voltage, current and harmonic data to a computer via Modbus RS485 interface. But this will be a bit of a do-it-yourself project.
For RCBO/GFCI nuisance tripping, often this will be linked to a switching transition -- something being connected to the system or switched on, that creates a transient unbalanced current in the live and neutral conductors. For LED flicker, it's traditionally associated with unstable timing of 'phase cut' dimming: the lighting driver is interacting with the dimmer. If you really want to see what is going on you will want the oscilloscope, but you will need to convert the current signal you want to observe to a voltage signal. As electrician, you would be confident making up a circuit breakout box with a CT and suitable burden resistor inside? You might make a specific one for measuring residual current -- look for a 'zero sequence CT', which has higher sensitivity.
Multiple times on the forum we discuss safe connection of oscilloscope to mains. The current transformer appropriately terminated will be ok. Differential voltage probes are great (but relatively expensive, unless you land one second-hand). You can use a voltage transformer to keep voltage measurement simple, but won't be super-accurate for observing some of the transient events. Battery powered oscilloscopes from Fluke are purpose-made, but they are really expensive, even for really old ones.
For RCBO/GFCI nuisance tripping, often this will be linked to a switching transition -- something being connected to the system or switched on, that creates a transient unbalanced current in the live and neutral conductors. For LED flicker, it's traditionally associated with unstable timing of 'phase cut' dimming: the lighting driver is interacting with the dimmer. If you really want to see what is going on you will want the oscilloscope, but you will need to convert the current signal you want to observe to a voltage signal. As electrician, you would be confident making up a circuit breakout box with a CT and suitable burden resistor inside? You might make a specific one for measuring residual current -- look for a 'zero sequence CT', which has higher sensitivity.
Multiple times on the forum we discuss safe connection of oscilloscope to mains. The current transformer appropriately terminated will be ok. Differential voltage probes are great (but relatively expensive, unless you land one second-hand). You can use a voltage transformer to keep voltage measurement simple, but won't be super-accurate for observing some of the transient events. Battery powered oscilloscopes from Fluke are purpose-made, but they are really expensive, even for really old ones.